Parallel arc or short circuit?

Steel480

Electrician
Location
USA
Occupation
Electrician
If a paralell arc the same thing as a short circuit? So why would this not trip a standard circuit breaker? Ive read 120v paralell arcs will not arc unless actually touching. If this is the case wouldnt a standard breaker detect this?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
All arcs have impedance and can limit the current flow to a level that will not cause the OCPD to open the circuit. An arcing fault is not a solid short circuit.
 