Parallel Breakers

ohmti787

Member
Location
Orlando, FL
Occupation
Electrical Engineer
Hello, I'm trying to feed a 400A ATS from a 400A meter main combo paralleling the two outputs of the meter main. Would this set up violate article 240.8?

Screenshot 2023-07-06 121215.png

I'm just going back and forth with the electrician on this. He's telling me that it's alright, that he's done it before and what not, but I don't know.... it seems kinda sketchy to me.

Please let me know your thoughts.

Thanks
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
You are correct, and he is not. He does not want to pull a permit and do it correctly or can’t/won’t get two 200 amp transferswitches. (Assuming your feeding two separate 200 amp panels.
 

ohmti787

Member
Location
Orlando, FL
Occupation
Electrical Engineer
It's an existing system. Currently the ATS feeds a MLO panel with two 150A CB's that feed two separate panels. Kinda of a mess actually
 

ohmti787

Member
Location
Orlando, FL
Occupation
Electrical Engineer
So, correct me if I'm wrong, but the hazard here is essentially the potential to backfeed this meter main, right?
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
That would not be possible per your drawing, assuming the transfer switch is correctly designed.

It is simply the performance of breakers in parallel is unknown.
Correct. Although breaker manufacturers can test and list parallel breakers for higher currents, you can’t do that in the field.

Well I suppose you CAN if you were willing to spend ~$50,000 with UL for the testing and listing…
 