Jsim4109
Member
- Location
- Cherry Hill, NJ,USA
The drawings on our project call for a 1600Amp Feeder with (4) sets of 3/C#500 Tray Cable per phase. They terminate on a 1600Amp Frame Circuit Breaker. The typical equipment grounding conductor that comes with this tray cable is a #2Awg Copper. According to Table 250.122, this feeder must be installed with a 4/0 Copper. The local inspector is not allowing us to use this cable because the smallest cable allowed in parallel is 1/0. I know there is an exception to 250.122 for multi-conductor cable. Let me know if anyone has any ideas other than ordering custom cable.