Parallel Cable Run

Status
Not open for further replies.
Location
Minneapolis, MN
Occupation
Electrical Engineer
Hi there,
I want to confirm one thing I made with the project I'm working on, So I have a large Panel (480/277V - 600A MCB) that I'm feeding from a switch board, and I'm wiring it with this configuration:

2* (4-1/C 350 KCMIL PH)
2* (1 AWG GND) XHHW-2, CU
2* (3" RGS CONDUIT)

Am I doing it right? also do we need 2 neutral and 2 ground wires for this parallel cable run? or one of each would be enough. Please let me know what you think, Thanks!
 
Each conduit must contain all phases, grounded and, if used, equipment grounding conductors,
Parallel conductors must not be smaller than 1/0
 
My comment on the parallel was simply to point out that Code Section and did not mean to indicate EGC. Poor wording on my part,
 