Industrial 4000 amp, 480 V, 3 phase service with no neutral load. HRG system to be connected to transformer neutral. Client would like to use multiple 3/C IAC (type MC) armored cables to connect an exterior utility transformer to the indoor switchgear with 4000 Amp main breaker. Cables to be installed in ladder tray, maintaining one diameter spacing between cables. Per table 310.15(B)(16) the ampacity of 500 MCM copper (90 C) would be 430 A, implying that 10 cables (or 11 if limited to 75 C) would seem to be adequate, before any derating. However, because the utility transformer will be a pad mount, some portion of the run will have to be underground (probably less than 10 feet, still in tray). Centerline of transformer and switchgear to be the same in order to make sure cables are the 'same' length. Total length of run probably less than 50 feet. What, if any, derating factors should apply?