Multiple Cables and One Fails
Multiple Cables and One Fails
It can happen. A compression fitting can corrode. A bolted joint can loosen. Even if it does not totally open circuit, I have seen enough cases of one conductor not sharing it's portion of the load. As a result, the other remaining conductors carry more than their rating. Eventually, something overheats and fails.
You can get fancy with protective schemes, zero sequence CTs on each cable run, etc. This is a case where periodic infrared imaging will hopefully catch the problem before a failure occurs.