I would like to know if "by code" the following can be done. My boss wants me to install a switched circuit (stand alone red flashing light to alert those in a room of visitors) in parallel off of an existing bank of lights (one circuit breaker). He says this will allow us to use the light switch for the lights and independently switch on the red light and only have to use one circuit..
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
one breaker = one branch circuit. You can do any type switching, etc with that branch circuit that you desire.
 

broadgage

Senior Member
Location
London, England
if your referring to using the switch leg of the room lights to feed another switch for your red light its OK but when the room lights are off the red light is dead (If thats what you mean)

Agree, but it might be an unwise design choice.
What if the room occupants have turned out the lights (perhaps to view video) but still wish to be advised via the red light light, of visitors ?
Unless there is some special reason to take the supply from the load side of the existing switch, I would be inclined to use the line side of the switch, so as to ensure that the red warning light works regardless of the room lighting.

I would also suggest that a red light might be unwise, and possibly in violation of fire safety codes.
Red lights are often connected to fire alarms to give warning to the deaf or in noisy enviroments.
White, yellow or green might be a better design choice.
 