boater bill
Senior Member
- Location
- Cape Coral, Fl.
A mechanical contractor is wanting to change out a specified 6 ton condensing unit for 2-3 ton units in the field, (cost). This will affect 5 units for a total of 15 new breaker slots needed. The electrical loads for the panel won't be an issue but the number of spare breaker slots are. There is not enough room in the electrical room to have a sub-feed panel either.
Does anyone know of a Code or other problem with having the previously specified 60 amp breaker and #6 conductors run to a disconnect between the units and subfeeding the units from there. each unit would have their own 30 amp disconnect at the units. The run from the electrical panel to the disconnect will be about 50-60 feet. The buiding is under construction and to change the runs wouldn't be a significant problem in the field either.
Any thoughts?
Does anyone know of a Code or other problem with having the previously specified 60 amp breaker and #6 conductors run to a disconnect between the units and subfeeding the units from there. each unit would have their own 30 amp disconnect at the units. The run from the electrical panel to the disconnect will be about 50-60 feet. The buiding is under construction and to change the runs wouldn't be a significant problem in the field either.