I have an duct bank installation from 15KV gear
to a GSU. I'm running 9 #750MCM per phase in 9
PVC conduits. These are connected to the gear bus
with protection provided with the generator 3000A breaker. Per art. 250.122 there is a 400kcml ground conductor run in each of the 9 conduits.
The contractor asked if a bare copper conductor could be run instead of insulated cable. He is suggesting running #500MCM bare copper. I can't
find anything in the code disallowing this, but Iwanted to check with you guys.
Thanks
to a GSU. I'm running 9 #750MCM per phase in 9
PVC conduits. These are connected to the gear bus
with protection provided with the generator 3000A breaker. Per art. 250.122 there is a 400kcml ground conductor run in each of the 9 conduits.
The contractor asked if a bare copper conductor could be run instead of insulated cable. He is suggesting running #500MCM bare copper. I can't
find anything in the code disallowing this, but Iwanted to check with you guys.
Thanks