310.4(B) says Conductor Characteristics. The paralleled conductors in each phase, polarity, neutral, grounded circuit conductor, or equipment grounding conductor shall comply with all of the following: (1) Be the same length
(2) Have the same conductor material
(3) Be the same size in circular mil area
(4) Have the same insulation type
(5) Be terminated in the same manner
Existing feeder of 7 sets of 500's run underground with RHW insulation and is terminated in a SWBD on one end and an ATS on the other end.
Feeder will remain connected on the SWBD end, but needs to be extended to another SWBD elsewhere in the room overhead (disconnected from the ATS), and will use the gutter of the ATS as a raceway to go out the top. Plan is to butt splice (long barrel compression) same size / quantity THHN to the end of the RHW and run the THHN to the new SWBD.
Is the installation described above a violation of 310.4(B)(4)?
(2) Have the same conductor material
(3) Be the same size in circular mil area
(4) Have the same insulation type
(5) Be terminated in the same manner
Existing feeder of 7 sets of 500's run underground with RHW insulation and is terminated in a SWBD on one end and an ATS on the other end.
Feeder will remain connected on the SWBD end, but needs to be extended to another SWBD elsewhere in the room overhead (disconnected from the ATS), and will use the gutter of the ATS as a raceway to go out the top. Plan is to butt splice (long barrel compression) same size / quantity THHN to the end of the RHW and run the THHN to the new SWBD.
Is the installation described above a violation of 310.4(B)(4)?