I'm planning on installing a Meter Pack, Ring Style Meter Socket Covers, 1-Phase, 2 Meter Sockets, 120/240V AC, 200 AMP Socket Rating, 400 AMP Bus Rating service entrance panel. One 200 amp rated socket will be for a residential dwelling and the other 200 amp rated socket will be for AG use. Using 310.15(B)(7) I reduced the ampacity for the residential meter to 83% (166 amps) and added that to the AG load (200 amps) for 366 amps. According to table 310.15(B)(16) I can use 700 kcmil at 375 amps or after derating 80% for 4-6 current carrying conductors I can use parallel 250kcmil. 230 amps at 80% = 184 and 366 amps divided by 2 = 183. Am I missing anything? Thank you.