A co-worker had a service call the other day, lights flickering, loud rattling etc. when using a piece of equipment. He found the problem, lug on the breaker had melted and broken loose. Now comes the real problem. This a 225A breaker feeding two pieces of equipment in a room where there was originally one. Conduit size 1 1/2" with 3 - 1/0 and 3 - #1 paralleled for this 225A feed. Obviously this is wrong. What are the potential dangers with this setup? I'm thinking lower resistance on the 1/0 will cause it to carry more load than it's capable of handling and minimal on the #1 or would it divide evenly? This will be quite costly to replace plus downtime for them and they don't want to do it.