If I have a compressor that draws 467 amps and I feed it with 2 sets of 300s in parallel, do I derate due to 6 current carrying conductors and now I need 400s, or do I not have to derate because each pair is a considered a single conductor making a total of 3 conductors in the conduit? The 300mcm conductor size already takes into account the increase to 125% for continuous duty.
Thanks in advance