I am running a feeder from a pad mounted switchgear with a 500 amp main breaker in the gear using 3 parallel runs of 4/0 AL conductors, 250' into the house, where they will terminate into a distribution block. Using the inside tap rule I am planning to run to four 200 amp distribution panels grouped (230.71A) each with a 200 amp main breaker intalled.
Under the 2005 NEC I am not required to run a ground with the feeders from the switch gear to the house, I just need to bond the Ground Electrode Conductor and the feeder neutral at the service disconnects at the house.
Since I am using four 200 amp main disconnects, grouped in the same room, do I size my GEC (table 250.66) for the individual disconnects (#4 cu) or size it based on the three parallel 4/0 and bond it at the distribution block.
Under the 2005 NEC I am not required to run a ground with the feeders from the switch gear to the house, I just need to bond the Ground Electrode Conductor and the feeder neutral at the service disconnects at the house.
Since I am using four 200 amp main disconnects, grouped in the same room, do I size my GEC (table 250.66) for the individual disconnects (#4 cu) or size it based on the three parallel 4/0 and bond it at the distribution block.