Does anyone know if cable couplers (plug/receptacles) can be installed on parallel feeder cables (i.e. two sets of 500 kcmil each with a 400 amp rated plug/receptacle)? I can't find anything in the NEC that prohibits this.
Yes I have installed 3 systems like this. The cables would use a different table as flexible cable in free air so it transitioned from 3 sets to 2 sets in some cases using a tap box. Not considered a tap or anythingDoes anyone know if cable couplers (plug/receptacles) can be installed on parallel feeder cables (i.e. two sets of 500 kcmil each with a 400 amp rated plug/receptacle)? I can't find anything in the NEC that prohibits this.