NOV
Member
- Location
- Upstate NY
- Occupation
- IDC Electrical Review Engineer
For a 600A feeder, using the 75 deg C column, wouldn't parallel 300KCMIL be acceptable based on Article 240.4(B)? And would that also hold true for parallel 250KCMIL since at 75 deg C it's good for 510A and the next standard overcurrent device would be 600A? It seems like I always see parallel 350KCMIL specified for 600A, and it looks like it would be a pretty nice cost savings if the smaller conductors are permitted.