Re: Parallel conductors in same conduit
I am going to have to ask for a clarification, as I smell a miscommunication in the making.
When you mention parallel conductors in the same raceway, do you mean:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Three phase or single phase?</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Including a total of four or more current-carrying conductors in the same conduit?</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Putting only the parallel Phase A conductors in one conduit, all the parallel Phase B conductors in a second conduit, and putting all the parallel Phase C conductors in a third conduit?</font>
<font size="2" face="Verdana, Helvetica, sans-serif">The second question brings you to Bob?s point about derating. The third question is the real reason I am asking for a clarification. I have seen it done, or rather, I have seen the fire that it caused. It is not allowed.
What is the issue that you are trying to resolve?