I was recently asked by a contractor if they could run parallel 4/0 instead of a single set of 500kcmil (for a 400A feeder). And he wants to put them all in the same pipe.
Assuming we can do that within the limitations of the 40% rule, how many ground conductors are required. Do you just need the one in accordance with 250.122.
Also, as we will have a neutral, do I have to derate for 8 current carrying conductors?
Thanks,
Mike
Assuming we can do that within the limitations of the 40% rule, how many ground conductors are required. Do you just need the one in accordance with 250.122.
Also, as we will have a neutral, do I have to derate for 8 current carrying conductors?
Thanks,
Mike