Found an existing installation on a 240v delta high leg system. Two sets of paralleled conductors, some are 250MCM, some are 300MCM. I wasn't able to count quantities of each as it was hot.
So, what is the allowable ampacity of this feeder? It is currently fused at 600A (all three legs) and this is what I'd like to get from it, obviously that isn't possible. The primary problem I see is that current won't be evenly divided between the different size conductors. It is worth at least 255A (the ampacity of the 250MCM). Is there some legal way to calculate a higher allowable ampacity so it doesn't have to be removed?
Thanks!
So, what is the allowable ampacity of this feeder? It is currently fused at 600A (all three legs) and this is what I'd like to get from it, obviously that isn't possible. The primary problem I see is that current won't be evenly divided between the different size conductors. It is worth at least 255A (the ampacity of the 250MCM). Is there some legal way to calculate a higher allowable ampacity so it doesn't have to be removed?