Hi Everyone,
I'd like to get some input on 310.10(H) - Conductors in parallel
I had an electrician tell me that you cannot change the quantity of conductors in parallel or their size. (If they start as 6 sets, they have to end as 6 sets and the conductor size can't change). I don't see why it would be an issue if they were:
(1) the same length
(2) same conductor material
(3) same size circular mil
(4) same insulation
(5) terminated in the same manner
For example, could I start at my swbd with 2 sets of 500, transition to 3 sets of 350 for the run, and transition back to 2 sets of 500 at my panel? The circular mil does change, but all of the parallel sets would be the same.
I'm looking at using the parallel rated multiconductor connector. (Voltage drop, oversized conductors, circuit breaker lug issues).
Thanks in advance!
p.s. What do the 5 yellow/gold stars mean on a post?
I'd like to get some input on 310.10(H) - Conductors in parallel
I had an electrician tell me that you cannot change the quantity of conductors in parallel or their size. (If they start as 6 sets, they have to end as 6 sets and the conductor size can't change). I don't see why it would be an issue if they were:
(1) the same length
(2) same conductor material
(3) same size circular mil
(4) same insulation
(5) terminated in the same manner
For example, could I start at my swbd with 2 sets of 500, transition to 3 sets of 350 for the run, and transition back to 2 sets of 500 at my panel? The circular mil does change, but all of the parallel sets would be the same.
I'm looking at using the parallel rated multiconductor connector. (Voltage drop, oversized conductors, circuit breaker lug issues).
Thanks in advance!