Pretty sure I am right about this but wanted to double check. I have a 400 amp service with single 400 amp main. From there I have parallel 4/0 AL all in the same pipe - emt and then rigid - to 2 200 amp panels. Each conductor set lands in its own panel. The conduit is the EGC, the panels are in the same building as the service, and the 200's are main breaker although I cant see that that would effect anything. Code violation right? Dont have my book handy but parallel conductors must be joined at each end, and these cant be considered two feeders because they are supplied by the same ocpd. Right? Because the panels are main breakers and not MLO, I am thinking that maybe they were originally service panels but the service was redone and moving some time ago...