Parallel conductors to a 200 amp breaker.

Status
Not open for further replies.

frankft2000

Senior Member
Location
Maine
A customer is putting in a manufactured home 500' from the transformer. The meter location that they currently have is about 175' from the transformer fed with overhead wires. The power company handbook states for voltage drop, this application would require parallel 4/0's. the service will be a 200 amp service. on the home end since the load center comes installed I guess my best bet is to bring the parallel conductors into a j box then tap down to a single 4/0 entering the load center. This would look pretty ugly doing the same thing on the meter pedestal/pole. The customer does not want the power company to set a new pole with a transformer closer to the home. So my real question is what is the best way to terminate parallel 4/0's onto a 200 amp meter/main?.
 

frankft2000

Senior Member
Location
Maine
Well thats my question, lugs will not fit into a breaker hole, so how do you terminate 2 parallel wires into 1 breaker hole? Most times Milbank is the make. The 200 amp meter disco has not been purchased yet. (existing is 100 amp).
 
Last edited:

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
Well thats my question, lugs will not fit into a breaker hole, so how do you terminate 2 parallel wires into 1 breaker hole? Most times Milbank is the make. The 200 amp meter disco has not been purchased yet. (existing is 100 amp).

Won't you hit the meter base side first? Double lug there then a factory buss feeds your main?
 

frankft2000

Senior Member
Location
Maine
The meter base is fed from the power company. I have to run parallel feeds from the breaker on the pole to the load center in the home 275'. I've never seen a breaker that good be lugged onto on the load side. I'm going load side of the meter main to the load center in the home.
 

chris kennedy

Senior Member
Location
Miami Fla.
Occupation
60 yr old tool twisting electrician
The meter base is fed from the power company. I have to run parallel feeds from the breaker on the pole to the load center in the home 275'. I've never seen a breaker that good be lugged onto on the load side. I'm going load side of the meter main to the load center in the home.

I see, I reread your OP. How about a handhole near the home with Polaris Blue?
 