Hello,
with an install of running parallel conductors in phased conduits underground, When does one have to be concerned with inductive heating in the surrounding metal in the a concrete duct bank?
 

ron

Senior Member
I always worry about it so I do phase isolated ducts very infrequently.

Depending on the current going through the feeder, the inductive heating will radiate out from the ductbank inches to feet I would imagine.

Do they really need ferrous metal near the duct bank?
 

ron

Senior Member
I never understood the point of phased conduits. Your inductive reactance goes way up.

I'm sure the installation becomes more straight forward not having to mix, dress and re-dress the phases into their proper termination groupings. Most folks don't care about inductive reactance (or even care what it means)
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
I always worry about it so I do phase isolated ducts very infrequently.

Depending on the current going through the feeder, the inductive heating will radiate out from the ductbank inches to feet I would imagine.

Do they really need ferrous metal near the duct bank?

IMHO phased conduits make for a much cleaner and neater install and for places where power continuity is important I would think this would be a better install method due to the fact that if two conductors fault in the same conduit, power is maintained.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
IMHO phased conduits make for a much cleaner and neater install and for places where power continuity is important I would think this would be a better install method due to the fact that if two conductors fault in the same conduit, power is maintained.


Iwire used to have a great picture that showed 12 pvc conduits coming in underground to a Main switchgear each with the phase conductors in it. It was clear that the phase A conduits being under the phase A lugs, etc made for a much neater install
 

kwired

Electron manager
Location
NE Nebraska
I never understood the point of phased conduits. Your inductive reactance goes way up.

Three large conduits (with all same phase within) vs three large conductors with similar grouping won't give you somewhat similar results? You want to keep close proximity between raceways. If only three raceways (plus a neutral where necessary) put them so they are as close as possible in trench they act like one big cable to some extent.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Hello,
with an install of running parallel conductors in phased conduits underground, When does one have to be concerned with inductive heating in the surrounding metal in the a concrete duct bank?
As long as the steel does not pass between the conduits, it is not an issue.
 