Parallel conductors

Status
Not open for further replies.

lauraj

Senior Member
Location
Portland, Oregon
Purely theoretical question here:

If you are installing isolated phase parallel conductors in conduit as permitted by 300.3(B)(1) exception into a metal bottomed enclosure, you have to cut a slot between the conduits per 300.20(B).

What about the metal locknut? Does that act as an inductive choke?
 
Re: Parallel conductors

The two times I have been directly involved in isolated phase arraignments as described in 300.20(B) Exception we did not use lock nuts.

I can not imagine using that exception in combination with metal bottomed enclosures.

The exception only applies to underground conductors which IMO suggests open bottomed switchgear will be the only option.
 
Re: Parallel conductors

I agree with Iwire, the times I have done this type of underground installation, it has always been in open bottom gear.

In a metal bottom enclosure you could use aluminum locknuts or a PVC chase nipple into a coupling for a couple of options.

Roger
 
Re: Parallel conductors

I agree with Roger's agreeing with Iwire. :)

To elaborate on what Roger said regarding aluminum locknuts, you could use any locknut that is non-ferrous (no iron).
 
Re: Parallel conductors

I also have installed this type of installation, but never to a metal bottom enclosure.
I guess I would probably have cut the bottom out of that enclosure.
I would also look at the installation instructions for that enclosure, sometimes you will see it says "top feed only". We have just such a scenario from a fair sized job here. The pipes are already installed underground, and I was reading the installation instructions for the equipment and it says "top feed only".
What a surprise... they were not happy I found that.
 