PARALLEL CONDUCTORS

Status
Not open for further replies.
Two(2) sets of 4-3/0 XHHW-2 + 1-1/0 G in one(1) 4 inch Schedule 40 PVC underground conduit. Is this allowed?

Thanks in advance for the answers.
My answer:

Likely the answer is yes but there might be some specific circumstances that would change that answer.
 
You have plenty of room
4 " Pvc = 5.022 sq. in
3/0 = .2642 x 8 = 2.1136
1/0 = .1825 x 2 = .3650

you can see there is plenty of room. You can get 19 - 3/0 xhhw-2 conductors in 4" pvc
 
My answer:

Likely the answer is yes but there might be some specific circumstances that would change that answer.
Yes tYes this is feeder of from a 150Kva pad mounted xformer supplying a panelboard MDP inside a building approx 160 lf from xormer , panel board main breaker 400 AT , load computed 260 Ampereshis is feeder of from a 150Kva pad mounted xformer supplying a panelboard MDP inside a building approx 160 lf from xormer , panel board main breaker 400 AT , load computed 260 Amperes
 