2 questions:
- 600 amp feed from a generator. I want to run 3 sets of 3/0. Is there an advantage/disadvantage to doing that instead of 2 sets of 350's? It will be a long run, underground, up the side of the building, through a large attic, and out the other side. And I have minimal help. I want to make this as easy as possible.
- The EGC. My understanding is that the EGC must be sized based on the OCPD, not paralleled like the phase conductors, so per 250.122 that would be 1 awg. Is an EGC required in each raceway, or only in one? Sorry for the rookie question on this, but it's been a minute since I did a parallel run, and I'm drawing a blank on how we did it.
Thanks.
- 600 amp feed from a generator. I want to run 3 sets of 3/0. Is there an advantage/disadvantage to doing that instead of 2 sets of 350's? It will be a long run, underground, up the side of the building, through a large attic, and out the other side. And I have minimal help. I want to make this as easy as possible.
- The EGC. My understanding is that the EGC must be sized based on the OCPD, not paralleled like the phase conductors, so per 250.122 that would be 1 awg. Is an EGC required in each raceway, or only in one? Sorry for the rookie question on this, but it's been a minute since I did a parallel run, and I'm drawing a blank on how we did it.