I have a question about feeding two devices each with 19.6A heaters (208V/1/60).
The heaters would be wired in parallel for the total load would be 19.6*2=39.2A.
The breaker would be 50A, (max breaker loading of 80%, 40A is greater than 39.2A so breaker ok).
Downstream of the breaker would be a 50A 2-pole contactor.
From the load side of the contractor, 2#6 (good for 75A from memory) wires to a j-box. From j-box, 2#10 wires (good for 30A) to each heater. All wire sizes are not corrected for temperature, conduit fill, etc. Just using straight values for example purposes.
Does this seem right? Do tap rules apply? Is overcurrent protection needed for each device (heater)?
If overcurrent protection is needed for each device, why would this situation be different than other circuits with multiple loads on it? Lights for example, often many lights are placed on a single circuit (one breaker).
Are devices wired in parallel considered taps?
Would things change (aside from load and possibly breaker and wire size changes) if the heaters were wired in 3-phase; one heater wired to L1-L2, second heater wired to L1-L3?
If this is not right, what would need to be done to wire the two 19.6A heaters to the 50A 2-pole contractor (in parallel)?
What specific sections of the NEC will help define the requirements for this situation?
Thanks!!
NH
I have a question about feeding two devices each with 19.6A heaters (208V/1/60).
The heaters would be wired in parallel for the total load would be 19.6*2=39.2A.
The breaker would be 50A, (max breaker loading of 80%, 40A is greater than 39.2A so breaker ok).
Downstream of the breaker would be a 50A 2-pole contactor.
From the load side of the contractor, 2#6 (good for 75A from memory) wires to a j-box. From j-box, 2#10 wires (good for 30A) to each heater. All wire sizes are not corrected for temperature, conduit fill, etc. Just using straight values for example purposes.
Does this seem right? Do tap rules apply? Is overcurrent protection needed for each device (heater)?
If overcurrent protection is needed for each device, why would this situation be different than other circuits with multiple loads on it? Lights for example, often many lights are placed on a single circuit (one breaker).
Are devices wired in parallel considered taps?
Would things change (aside from load and possibly breaker and wire size changes) if the heaters were wired in 3-phase; one heater wired to L1-L2, second heater wired to L1-L3?
If this is not right, what would need to be done to wire the two 19.6A heaters to the 50A 2-pole contractor (in parallel)?
What specific sections of the NEC will help define the requirements for this situation?
Thanks!!
NH