Can you run a pair of tens in lieu of an eight in a single run of conduit? Never thought of it before.
None really. Depending on how you read it, 250.122(F) could be interpretted as allowing parallel EGC's... but how do you get past the sizing requirement? All you'd end up doing is installing two or more of the minimum required size... not like your OP example using 2-10's instead of an 8.Charlie, what code prevents paralleling EGCs smaller than 1/0?
How does the specific permission in 310.4 act to prohibit any other installation?300.3(B) is what allows paralleling in the first place. It says to do it in accordance with 310.4. So we can't do it in any way that is not described in 310.4.
What 310.4 says is that it is acceptable to parallel (essentially) just phase and neutral conductors. It does not explicitly say this, but it is commonly understood that by paralleling two phase conductors, we get twice the ampacity. Then, when 310.4(E) mentions paralleling EGCs, it tells us to use a full size version in each conduit. So 310.4(E), at least, is not allowing us to combine smaller EGCs to get the value of a larger EGC. And that brings me back to 310.4. The absence of EGCs in a list that gives us the ability to use two smaller wires to gain the benefit of a single larger wire tells me that paralleling EGCs is not allowed.
How does the specific permission in 310.4 act to prohibit any other installation?
How does the specific permission in 310.4 act to prohibit any other installation?
... shall be permitted to be connected in parallel (electrically joined at both ends) only in sizes 1/0 AWG and larger
Please define, give an example, elaborate or otherwise clarify what you mean by other installation.How does the specific permission in 310.4 act to prohibit any other installation?
I noted 310.4(E) above, but that's from 2008 NEC.It is an odd thing because 310.10(H)(1) states 1/0 for everything other than the equipment grounding conductor. So does that mean the equipment grounding conductor can be paralleled in smaller sizes??? 310.10(H)(3) specifically states that the equipment grounding conductor is allowed to be run in parallel.
So did they just forget to add the equipment grounding conductor in the first part or does it mean we can parallel equipment grounding conductor smaller than 1/0. Maybe if I understood why conductors of 1/0 and larger are only allowed to be in parallel I could better answer the question.
My take is that the NEC would prefer not having parallel wires so they limit it where it obviously isn't necessary to do so based on wire sizes. This would limit the margin of error that the parallel conductors may have.
If that is the case then I would suspect the equipment grounding conductor should not be paralleled smaller than 1/0.
(5) Equipment Grounding Conductors. Where parallel
equipment grounding conductors are used, they shall be sized
in accordance with 250.122. Sectioned equipment grounding
conductors smaller than 1/0 AWG shall be permitted in multiconductor
cables in accordance with 310.104, provided the
combined circular mil area of the sectioned equipment
grounding conductors in each cable complies with 250.122.
My point is, that prior to the 2011 code, the code did not actually prohibit the paralleling of conductors smaller than 1/0.(yes, we all know that was the intent, but the code language did not reflect that intent, there is new wording triggered by a proposal of mine in the 2011 code that added to word only... it comes closer to reflecting the intent, but am not convinced it actually does)Please define, give an example, elaborate or otherwise clarify what you mean by other installation.
310.4 general statement doesn't mention EGC's and uses the terminology "shall be permitted", yet under 310.4(E) paralleled EGC's "shall be" sized per 250.122, and only sectioned EGC's in multiconductor cable "shall be permitted" smaller than 1/0...
PS: I hereby retract my "None really" comment in post #4.
It is an odd thing because 310.10(H)(1) states 1/0 for everything other than the equipment grounding conductor. So does that mean the equipment grounding conductor can be paralleled in smaller sizes??? 310.10(H)(3) specifically states that the equipment grounding conductor is allowed to be run in parallel.
So did they just forget to add the equipment grounding conductor in the first part or does it mean we can parallel equipment grounding conductor smaller than 1/0. Maybe if I understood why conductors of 1/0 and larger are only allowed to be in parallel I could better answer the question.
My take is that the NEC would prefer not having parallel wires so they limit it where it obviously isn't necessary to do so based on wire sizes. This would limit the margin of error that the parallel conductors may have.
If that is the case then I would suspect the equipment grounding conductor should not be paralleled smaller than 1/0.
I understand and agree. In order for ""shall be permitted" to act like an exception, there has to be rule which otherwise prohibits what the exception permits.My point is, that prior to the 2011 code, the code did not actually prohibit the paralleling of conductors smaller than 1/0.(yes, we all know that was the intent, but the code language did not reflect that intent, there is new wording triggered by a proposal of mine in the 2011 code that added to word only... it comes closer to reflecting the intent, but am not convinced it actually does)
There was no rule that said you could not do that. Telling me that I can do something, does not create a restriction on doing something else. The term "shall be permitted" is intended to act like an exception to some rule.
I agree, essentially... but there are no "Exceptions" regarding paralleled EGC's. There is no requirement for parallel EGC's to be 1/0 or larger.Example: we have a 400 amp circuit that consists of parallel 3/0 conductors in separate raceways. If we run an EGC we must run one in each raceway, but 250.122 says 3AWG is sufficient for 400 amp OCPD - each raceway needs full sized EGC which is 3 AWG minimum. Or must the EGC's be 1/0 because they are parallel to one another? (I think exceptions allow the 3 AWG here)
Example: we have two or more raceways between two enclosures, none of the contained circuits are over 30 amps so 250.122 says 10 AWG for 30 amps OCPD. Can we run 10 AWG in these raceways for EGC or must they be 1/0 since they are parallel to one another? Big difference in size of raceway needed to accommodate the EGC if we only needed 1/2 or 3/4 before determining the EGC must be 1/0. (I think exceptions allow the 10 AWG here)
In the 2008 and earlier codes, there is no requirement for any paralleled conductor to be 1/0 or larger.I agree, essentially... but there are no "Exceptions" regarding paralleled EGC's. There is no requirement for parallel EGC's to be 1/0 or larger.