hey_poolboy
Senior Member
- Location
- Illinois
Went on a service call today that involved a GFCI tripping. Seems as though the spa breaker would trip at very irregular intervals. The spa had a factory recommended 60a GFCI but the spa was three wire. The installer ran 6/3 UF to the spa and hooked the grounded conductor to the load neut. on the GFI, but at the tub it was just taped off and the spa has no place on which to terminate it.
Now the questions.
1. would this possibly act as an "antenna" and trip the GFI from incuced voltage on the grounded conductor?
2. If so, how can it be fixed?
3. If I land both ends of the conductor with the EGC and create a parallel EGC is that OK?
4. Would it be better to leave it un-terminated on both ends?
Any help would be greatly appreciated
Thanks,
Mike