Re: Parallel Equipment grounding conductor size
Have you seen the price of copper lately..
also, if you have an estimating program, run both ways through. the smaller the conductor, the less resistivity lost, the easier to pull, no tugger etc. how many amps is a 500 kcmil good for? now look at a 1000 kcmil, notice a problem. Now, in 96' and older NEC, there was a specific exception that stated the grounding conductor shall not be required to be larger than the ungrounded conductor. It was not until 99' that it was restructured to the "general" note that now covers all area A-F including motors. I think the guy is ahead of the curve.