JohnHurst
Member
- Location
- Las Vegas, NV
I work for a company that designs and manufactures motor controller equipment. Since our development lab is in a facility that only has 208V 3-phase available, we are running through a step-up transformer to get 480V to play with. Because things sometimes go wrong with new designs
, and we occasionaly blow the fuses/breakers in the electrical room (to which we don't have private access), we installed two separately metered 200A service panels that feed the same lugs on the transformer. The thought being that, if we trip the breaker in the electrical room on one disco, we can - after correcting the problem in our device - switch over to the other disconnect and continue on while we wait for the landlord to reset the original breaker. This arrangement works fine.
My question is this: If I were to turn on both disconnects at the same time, would that essentially double the current available to me to 400 amps? The transformer is rated for it, so that's not a problem. The conductors are all properly phased, so my first guess is that I would simply have 400 amps available at the primary. I'd rather not have to install a 400 amp service if I can avoid it, as I will only have a very occasional need for that much power.
My question is this: If I were to turn on both disconnects at the same time, would that essentially double the current available to me to 400 amps? The transformer is rated for it, so that's not a problem. The conductors are all properly phased, so my first guess is that I would simply have 400 amps available at the primary. I'd rather not have to install a 400 amp service if I can avoid it, as I will only have a very occasional need for that much power.