electro7
Senior Member
- Location
- Northern CA, US
- Occupation
- Electrician, Solar and Electrical Contractor
I think I did this wrong and was wondering if I could get some input?
I have a 600A MCB in a switchgear cabinet, 120/240V single phase. We are coming off the load side of breaker to an ATS (600A) and back out of the ATS to the distribution. We ran 2 sets of 350 kcmil parallel conductors in the same conduit. My original thought was 2 350 kcmil would have an ampacity of 620A at 75C- (not thinking about circular mils).
It dawned on me the other day that I may have calculated this wrong and need to look at circular mils. When I do that calc 2 350 kcmil comes to 354 circular mils which is equal to just under 700 kcmil (355 circular mils). 700 kcmil ampacity is only 460A at 75C.
I was wondering if somebody can help me to know if the 2 350 kcmil conductors paralleled is okay or not okay?
If not okay, I was thinking about downsizing the main breaker to 500A to save thousands $ in conductors. I thought I could go to NEC310.15(A)(7) to leave the 350 kcmil conductors in and downsize the main breaker to 500A, but saw the 83% rule is only for 100A-400A.
Needing some help on this one. Thanks ahead of time!
I have a 600A MCB in a switchgear cabinet, 120/240V single phase. We are coming off the load side of breaker to an ATS (600A) and back out of the ATS to the distribution. We ran 2 sets of 350 kcmil parallel conductors in the same conduit. My original thought was 2 350 kcmil would have an ampacity of 620A at 75C- (not thinking about circular mils).
It dawned on me the other day that I may have calculated this wrong and need to look at circular mils. When I do that calc 2 350 kcmil comes to 354 circular mils which is equal to just under 700 kcmil (355 circular mils). 700 kcmil ampacity is only 460A at 75C.
I was wondering if somebody can help me to know if the 2 350 kcmil conductors paralleled is okay or not okay?
If not okay, I was thinking about downsizing the main breaker to 500A to save thousands $ in conductors. I thought I could go to NEC310.15(A)(7) to leave the 350 kcmil conductors in and downsize the main breaker to 500A, but saw the 83% rule is only for 100A-400A.