Here is the installation: 480v 8000 amp service. Draw-out breakers.
Breaker 1 2000 amp, feeds MCC Main Breaker 2000amp. 5 parallel sets of 500 MCM, run with 5 parallel sets of 4/0 EGC. All run in a cable tray.
The EGC raised a red flag to me, so I checked on it when I got home and I believe that this is an undersized EGC.
250.122(F)(1) Each parallel EGC shall be sized on the basis of the ampere rating of the overcurrent device protecting the conductors...
I think that table 250.122 says EGC 2000amp 250kcmil.
Now we also pulled a 4/0 EGC for the 800amp main breaker which is oversized
I mentioned this to the foreman and I was told that I was wrong.
Am I interpreting this wrong?
Breaker 1 2000 amp, feeds MCC Main Breaker 2000amp. 5 parallel sets of 500 MCM, run with 5 parallel sets of 4/0 EGC. All run in a cable tray.
The EGC raised a red flag to me, so I checked on it when I got home and I believe that this is an undersized EGC.
250.122(F)(1) Each parallel EGC shall be sized on the basis of the ampere rating of the overcurrent device protecting the conductors...
I think that table 250.122 says EGC 2000amp 250kcmil.
Now we also pulled a 4/0 EGC for the 800amp main breaker which is oversized
I mentioned this to the foreman and I was told that I was wrong.
Am I interpreting this wrong?