So as I examine one of a complex of industrial buildings, I realized the power misspoke and what I thought was a 150kva 480/277 Xfmr, is a 208/120. Power comes in as parallel conductors into a trough where it goes into a distribution block, then broken off of that immediately into 3 main disconnects, so there is not a single main disconnect that carries all the load. Why they would bring in 208/120 into a large industrial space is beyond me! I might have to consider a higher voltage upgrade at some point but for now, I need to move about 400A of 208 about 50ft. I would either repurpose one of the main disconnects, or replace. Either way, the legs between the service distribution lug and the first disconnect would have to be either upgraded or paralleled to allow the higher ampacity. I was really trying to avoid a utility service disconnection for this work but the only other option is working it hot...... Work has to get done on that distribution lug, possibly even replacing it for the expansion.
Once I can get enough power to a disconnect, I need to run power about 50ft and I have priced either 750mil or a parallel 4/0 triplex. I was hoping to move 400A but appears due to derates (20% for 3-6 connductors), I land at just under 350A in which I had hoped it would be higher so I could use the 'next size up rule' to set it at 400A. for instance, 4/0Al is 205A at 90c, and with 20% derate, 164A*2 = 328. I think 750 was 348A.
Since I don't remember the last time I had to do a parallel run, I was wondering if there are other complicating factors other than 2 having to run 2 conduit runs? The conduit fill for 1.5" hits 40.16%!! So I get to bump to 2" over .16%?
At this point, i am probably not too concerned about running A neutral in this and would do that another way. 120V loads are not too important right now.
I was trying to stick with 4/0 mainly due to the price as a common triplex cable size.
Once I can get enough power to a disconnect, I need to run power about 50ft and I have priced either 750mil or a parallel 4/0 triplex. I was hoping to move 400A but appears due to derates (20% for 3-6 connductors), I land at just under 350A in which I had hoped it would be higher so I could use the 'next size up rule' to set it at 400A. for instance, 4/0Al is 205A at 90c, and with 20% derate, 164A*2 = 328. I think 750 was 348A.
Since I don't remember the last time I had to do a parallel run, I was wondering if there are other complicating factors other than 2 having to run 2 conduit runs? The conduit fill for 1.5" hits 40.16%!! So I get to bump to 2" over .16%?
At this point, i am probably not too concerned about running A neutral in this and would do that another way. 120V loads are not too important right now.
I was trying to stick with 4/0 mainly due to the price as a common triplex cable size.