Parallel Feeder Sizing

Status
Not open for further replies.

sniperracingcf

New member
How do you size parallel feeders. Im sure theres a formula for this and I just cant remember it. For example I have a 600 amp single phase service that I want to parallel ALU feeders to but cant remember how to. Any help would be great. Thanks
 
I know of no formula as such. As a base you would use the ampacity of the conductor X the number of conductors.
As with single conductors you need to take into account termination restrictions (110.14) and and derating factors.
The only added consideration in paralleling is if you share a conduit you must remember to apply the rules of 310.15(B)(2) (as you would on single runs when applicable)
You will probably end up with 500kcmil for 600 amps, but it depends on the caluclated load, derating factors, such as ambient, number of conductors (3 phase vs single; neutral or not) and if you are sharing one conduit.
There is no simple, one-step formula.
 
Last edited: