Would it be a violation to feed two seperate 400A discos, which in turn feed two transformers, which each have their own panel, from one three pole 800A breaker? Assuming balancing was not an issue.
Just wondering if anything would prevent bringing one run into each disco directly.
No, and might be preferable. It would certainly be easier to wire.Just wondering if anything would prevent bringing one run into each disco directly.
Welcome to the forum!
No, and might be preferable.
I have never noticed a current rating on the connectors but always figured they were good for at least the rating of the maximum wire size.
Did you connect the lines to ports 1-4 and the loads to ports 5-7
or did you alternate line/load.
I have never noticed a current rating on the connectors but always figured they were good for at least the rating of the maximum wire size. If all of the lines were connected to one end and all of the loads to the other end the middle of the connector would need to carry 1200 amps.
Quite intriguing subject. If determined by bus sizing as a "guide", the cross sectional area would have to be 1.2 in? Cu to carry 1200A at any point. Line-load staggered would definitely be the better approach.Bob, I'm curious how you made the connections to the Polaris. Did you connect the lines to ports 1-4 and the loads to ports 5-7 or did you alternate line/load. I have never noticed a current rating on the connectors but always figured they were good for at least the rating of the maximum wire size. If all of the lines were connected to one end and all of the loads to the other end the middle of the connector would need to carry 1200 amps.
Assuming a 2x1 out, the one would best be placed in the middle hole.
...and of the three outs 2 went to one disco while one went to another... 2x1 out.I had seven ports, 4 IN, 3 OUT.
I'm sure this info makes everyone more comfortable with your use of the connectors... but staggered is still the better approach. Don't you agree?I also know from a months worth of recording that the entire load carried by these connector does not exceed 700 amps.
but staggered is still the better approach. Don't you agree?
Bob, I first want to state that I wasn't stating that you did anything wrong.
I just checked Ilsco's web site since they now makes a similar connector and below are the specifications.
- Broad wire range: 750kcmil-14
- UL Listed and CSA certified for 600 volts, 90?C
- Dual rated for copper or aluminum conductor
- Cold temperature rated to -45?C
- High dielectric strength plastisol is chemical resistant
- Black cover is UV rated
- Removable port & screw plugs
- Prefilled with De-ox
- Per NEC Article 310-16 Allowable Ampacities are as follows: # 4 - 95 Amps, 1/0 - 170 Amps, 3/0 - 225 Amps, 250 - 290Amps, 350 - 350 Amps, 500 - 430 Amps, 750 - 535 Amps
- Incoming and outgoing conductors must be staggered.
- UL File E6207
Well thats interesting.
Bob, the taps in your picture are polaris.