myntz
- New Jersey
- Engineer
First time posting here, so I apologize if there are standards that I am not following. I have a 1600A feeder that needs to be pulled via conduit and then transition into cable tray. I have 5 sets of 350MCM and I have adjusted trip unit to dial it down to meet the ampacity. I understand that for parallel feeder via conduit, each conduit will need an equipment ground conductor. I also understand that for cable tray, a single equipment ground conductor is sufficient. Am I allowed to run 5 EGC via conduit and then "splice" it into the single EGC in the cable tray? Would this violate 310.10(g)(2)? How do you handle EGC when you have parallel feeders transition from conduit to cable tray?