parallel feeder

Status
Not open for further replies.

tmb

Member
I have pumps , each pump feeder , multicores 2 cables 120 mm2 ,, 2( 3x120 mm2 ) , it is allwed to run each feeder in 2 conduits .UPVC or EMT .
 
Re: parallel feeder

I am not sure I understand your question. But you can run parallel feeds to just about any load. Make sure that each conduit has one set of all phase conductors, a neutral, and an equipment grounding conductor. Also be sure to size the equipment grounding conductor correctly. It is size based on the ocpd when run in parallel feeds.
 
Re: parallel feeder

I am not sure I understand your question. But you can run parallel feeds to just about any load.
keeping 310.4 into account (minimum 1/0)
if my math is right, your wire meets the requirment...just clarifying
 