parallel feeder
tmb
I have pumps , each pump feeder , multicores 2 cables 120 mm2 ,, 2( 3x120 mm2 ) , it is allwed to run each feeder in 2 conduits .UPVC or EMT .
Re: parallel feeder
I am not sure I understand your question. But you can run parallel feeds to just about any load. Make sure that each conduit has one set of all phase conductors, a neutral, and an equipment grounding conductor. Also be sure to size the equipment grounding conductor correctly. It is size based on the ocpd when run in parallel feeds.
Re: parallel feeder
keeping 310.4 into account (minimum 1/0)
if my math is right, your wire meets the requirment...just clarifying