Parallel Feeders in nipples

Status
Not open for further replies.
Magnetic fields do not cancel, thete will be induced currents in the nipples, heating and possible fire. Do a thermal scan
 
All of the phases are required to be in each pipe for the reasons mentioned above. In situations where a ground wire is run in the pipe, a duplicate ground wire is required in each pipe.
 
That is oddly unfortunate... what if the engineer screwed up the pipe schedule...and he (clearly a meticulous wireman) didn't catch the mistake?
 
All of the phases are required to be in each pipe for the reasons mentioned above. In situations where a ground wire is run in the pipe, a duplicate ground wire is required in each pipe.
A,B,C plus ground in each raceway.
 
Absolutely not. The wires coming into the left enclosure show it done correctly.

And when it's rewired, the three wires of each phase should remain the same length.
 
Compliant if the nipples, connectors and enclosures are non ferrous? That would (almost?) eliminate the inductive heating effects. The enclosures are probably ferrous, though.

Cheers, Wayne
 
Compliant if the nipples, connectors and enclosures are non ferrous? That would (almost?) eliminate the inductive heating effects. The enclosures are probably ferrous, though.
Yes, non-ferrous conduits and slots between holes would suffice.

I've often wondered why steel locknuts aren't an issue, though.
 
Code we don't need no stinking code!
This is one of those rules that illustrates the code is not an instruction manual. But the reason this can't be done is well grounded in electrical theory.
Brian John posted a picture some time ago of a similar installation, IR photo had the conduits red, IE, hot! I can't find the picture at the moment
 