Please tell me why.Absolutely not compliant.
A,B,C plus ground in each raceway.All of the phases are required to be in each pipe for the reasons mentioned above. In situations where a ground wire is run in the pipe, a duplicate ground wire is required in each pipe.
Yes, non-ferrous conduits and slots between holes would suffice.Compliant if the nipples, connectors and enclosures are non ferrous? That would (almost?) eliminate the inductive heating effects. The enclosures are probably ferrous, though.
Probably because of the small amount of magnetic material...can't make enough heat to be a problem.Yes, non-ferrous conduits and slots between holes would suffice.
I've often wondered why steel locknuts aren't an issue, though.
I agree, with use steel locknuts with MI cable connectors and cut slots between the conductors without any issues.Probably because of the small amount of magnetic material...can't make enough heat to be a problem.
Finally on post #14 we get a code section!300.3(B)(1).
Yeah I find that baffling.I do find it curious anytime I see such craftsmanship but a seeming lack of knowledge of fundamentals.