Parallel feeders

Status
Not open for further replies.
Location
NYC
Occupation
Electrician
Is it permissible to run aluminum parallel feeders terminate all sets in a multi tap connector & extend to a panel board in copper. Eg 2 sets 750kcm terminated on a 4 port bug with 2 sets 600kcm extended to panel.
 
Yes. Manufacturers instructions might require you to stagger the connections.
 
Would I be correct in saying that if the parallel conductors were extended individually (750al-600cu) this would be a violation.
 
The important thing is that the conductors of each paralleled set making up any given phase match in all characteristics and physical connections, to assure equal current sharing.
 