Existing emergency switchboard with two available 1600AF/1600AT breakers new 3200A switchboard located adjacent to it. In the current project they will be installing the new switchboard, with 3200A MCB the generator to feed this switchboard are to be included in a future project, for the time until the new generators are purchased would it be compliant to provide two 1600A feeders one from each of the breakers to the 3200AF breaker to supply emergency power to the board for the time until the new generators are purchased and installed (as part of the next phase / addition). Article 240.8 talks about circuit breakers and fuses in parallel but it is really the conductors that are being paralleled. Any thoughts?