I have a feeder that im tapping in a ct cabinet and extending . Can i run new conductors within same conduit . They are feeders for the same panel which is parallel fed.
I think your biggest problem will be complying with 310.4(B) especially 310.4(B)(1) if the conductors are relatively short.
Thanks; we're still on 2008 effectively in CA.FYI, they moved that article to 310.10(H)1-6 for the 2011 book.