Let's hope that the readings are additive. Because if not, that means there is probably a ground fault.
For a healthy feeder of multiple wires per phase, the total phase current is the sum of the current in each wire of that phase. And the current is divided equally, if they are constructed properly.
Here is an interesting problem for you, on the subject of parallel feeder conductor sets.
The NEC requires the parallel wires per phase to all be the same length, and have many other similar characteristics as well. However, in a practical sense, it isn't always possible to get them exactly the same length. Suppose you are a contractor who built a 500A feeder with two parallel sets of 250 kcmil Cu. One set of wires ran a length of 45 ft, and the other set of wires ran a length of 48 ft. The inspector notices this, and challenges you to prove whether or not it is a problem.
At the full 500A, what is the current in each set of this parallel feeder?
Will the ampacity of any of the conductors be exceeded?
Answers: 242A in the 48 ft set, 258A in the 45 ft set. YES, unfortunately.