J jbezz55 New member Location Houston Mar 11, 2008 #1 At what size feed does it make sense to run parallel conductors to motors. It seems from what I recall anything above 250MCM should consider running parallel feeds. What about the ecconmic factor also Jbezz:
At what size feed does it make sense to run parallel conductors to motors. It seems from what I recall anything above 250MCM should consider running parallel feeds. What about the ecconmic factor also Jbezz:
iwire Moderator Staff member Location Massachusetts Mar 11, 2008 #2 Normally we don't parallel till we pass 500 Kcmil. Certainly there are exceptions to that, some jobs layout better with multiple smaller conduits.
Normally we don't parallel till we pass 500 Kcmil. Certainly there are exceptions to that, some jobs layout better with multiple smaller conduits.
iwire Moderator Staff member Location Massachusetts Mar 11, 2008 #3 You should check out this thread Splitting large ampacity need across multiple smaller conductors - pros/cons (?) ( 1 2)
You should check out this thread Splitting large ampacity need across multiple smaller conductors - pros/cons (?) ( 1 2)