At what size feed does it make sense to run parallel conductors to motors.
It seems from what I recall anything above 250MCM should consider running parallel feeds. What about the ecconmic factor also

Jbezz:
 
Normally we don't parallel till we pass 500 Kcmil. Certainly there are exceptions to that, some jobs layout better with multiple smaller conduits.
 
You should check out this thread

Splitting large ampacity need across multiple smaller conductors - pros/cons (?) (