Are there any issues to parallel two generators at different size (kW)?:blink:
I don't know, but I do know how I would go about it.
I'm assuming you're talking big units, maybe for redundancy in a big standby bank
First I would consult the manufacturer's engineer and they should be able to tell you pretty quickly if it will or won't work, and why, what to look out for.
Don't quote me as I'm not the expert but: voltage regulators ...
One of the units VR will be set to "isochronous" or something like that. It will try to maintain frequency setpoint regardless of load. The other units VR will be set to " % of droop ", usually 5% droop. I believe, my understanding of how this works, is the VR will allow 5% voltage droop over the load range of 0% to 100% load, and this is how the units load share.
The lead unit set to isochronous maintains a fixed speed of rotation, and the droop units maintain a difference between the rotor angle and rotating field that determines unit loading.
There are enough variables and special expertise required that it may or may not work. Set up a caution tape and keep the clueless fakers away from it.
Edit: should have checked wikipedia. Droop control varies the rotation speed from 100% to 105% over the load range. and google "droop control".