akpdx
Member
- Location
- Washington Cty, OR
- Occupation
- Electrician
Hello! A bit of a rabbit-hole question about sizing grounded conductor run in parallel...I'm hoping someone can help me understand something. I'm looking at a problem with a calculated load for a multifamily dwelling just over 900 amps.
Service OCPD is 1000A
Paralleled service conductors - 3 sets of 400 kcmil Cu
Paralleled neutral minimum size as calculated is 152 amps - 2/0 Cu
Minimum grounded conductor according to Table 250.102 (C)(1) is 3/0 Cu
I have seen it said several times that a grounded conductor cannot be smaller than the grounding electrode conductor or an equipment ground.
Where in the Code does it say that? 250.24 (C) doesn't tell us anything about comparing it to any grounding conductor. Nor does 250.102.
What am I missing?
Service OCPD is 1000A
Paralleled service conductors - 3 sets of 400 kcmil Cu
Paralleled neutral minimum size as calculated is 152 amps - 2/0 Cu
Minimum grounded conductor according to Table 250.102 (C)(1) is 3/0 Cu
I have seen it said several times that a grounded conductor cannot be smaller than the grounding electrode conductor or an equipment ground.
Where in the Code does it say that? 250.24 (C) doesn't tell us anything about comparing it to any grounding conductor. Nor does 250.102.
What am I missing?