Paul Bates
Member
I recently inspected a 800 amp 120/208 volt main breaker service with parallel 500 mcm feeders. The grounding electrode run to the water pipe was a 1/0 cu in a metal conduit. I requested that the grounding electrode be changed to 2/0 Cu per NEC table 250.66. The contractor then installed an additional # 1 Cu wire with the 1/0 cu in the pipe and contends the circular mill area equals or exceeds 2/0 cu and therefore is OK. I contend that parallel conductors are only permitted in size 1/0 cu and larger per NEC 310.4Is this the only article to prohibit this installation and or is the installation OK?