A line to ground fault can be fed from each of the circuit. The EGC must be full size to carry the fault.
Leave out part of what you wanted to say there?A line to ground fault can be fed from each of the circuit. The EGC must be full size to carry the fault.
The ungrounded conductor that becomes faulted must also withstand the current, if you want the OCPD to trip before it burns out the conductor. But the ungrounded conductor often is larger than the EGC anyway. I won't say you can't run into needing a larger EGC than the ungrounded conductors, but would be pretty rare I would think.The withstand rating of the EGC has to be able to accommodate all of the fault current that the upstream fuse / breaker can let through until it opens.
It it was not full sized in each raceway, then a fault within an individual raceway would have a reduced sized EGC trying to carry the fault current by itself and burn-up until the OCPD clears the fault, which might be never at that point if the EGC can't maintain continuity.
The withstand rating of the EGC has to be able to accommodate all of the fault current that the upstream fuse / breaker can let through until it opens.
It it was not full sized in each raceway, then a fault within an individual raceway would have a reduced sized EGC trying to carry the fault current by itself and burn-up until the OCPD clears the fault, which might be never at that point if the EGC can't maintain continuity.
Section 250.122(A) indicates that EGCs never have to be larger than the ungrounded conductors of the circuit.The ungrounded conductor that becomes faulted must also withstand the current, if you want the OCPD to trip before it burns out the conductor. But the ungrounded conductor often is larger than the EGC anyway. I won't say you can't run into needing a larger EGC than the ungrounded conductors, but would be pretty rare I would think.
Section 250.122(A) indicates that EGCs never have to be larger than the ungrounded conductors of the circuit.
I agree except for parallel runs where the ungrounded conductor is the sum of all the parallel sets so you could end up with the EGC's in each parallel raceway that are required to be larger than the condcutors within each raceway.