I have a job that we are designing that will consist of upgrading an existing 1000 amp feeder to a 1200 amp feeder.
The existing feeder is 3 sets of 4-500kcmil & 1-2/0g.
The 2/0 ground is too small for a parallel ground per table 250.122. The ground size needs to be 3/0.
The neutral is not being used on the existing feeder and is not needed for the new feeder.
We want to disconnect the existing 2/0 grounds and disconnect the unused 500kcmil neutral.
We can either use the conduit as a ground or the now unused 500kcmil as the ground.
We will be adding another set of 3-500kciml and a 3/0g.
My question is, does the additional ground need to be a 3/0 or does it need to be sized the same as the other grounds at 500kcmil?
NEC 2008 250.122(F) does not specify.
The existing feeder is 3 sets of 4-500kcmil & 1-2/0g.
The 2/0 ground is too small for a parallel ground per table 250.122. The ground size needs to be 3/0.
The neutral is not being used on the existing feeder and is not needed for the new feeder.
We want to disconnect the existing 2/0 grounds and disconnect the unused 500kcmil neutral.
We can either use the conduit as a ground or the now unused 500kcmil as the ground.
We will be adding another set of 3-500kciml and a 3/0g.
My question is, does the additional ground need to be a 3/0 or does it need to be sized the same as the other grounds at 500kcmil?
NEC 2008 250.122(F) does not specify.