310.10 (H) (2) requires parallel conductors to be the same length. My confusion lies here: Is this the total overall length (ie. sum of line1+load1=line2+load2), or are we talking line/load sides needing to be equal (ie. line1=line2, load1=load2)?
Current example:
Switchgear with 2 UPS units paralleled in. In the drawings, the UPS1 input length is 18ft, output is 30ft; UPS2 input is 29ft, output is 20ft. Totals are 48ft and 49ft, within 3% for voltage drop. However, you've got an 11ft difference in your inputs, and a 10ft difference in your outputs, which would be way off. Alternatively, you can switch the breaker layout so that your UPS1 I/O lengths are 23/25ft, and UPS2 I/O lengths are 24ft/24ft, with totals at 48ft/48ft which is definitely okay for voltage drop.
Are they both right and the alt install unnecessary? Or are the drawings wrong?
Current example:
Switchgear with 2 UPS units paralleled in. In the drawings, the UPS1 input length is 18ft, output is 30ft; UPS2 input is 29ft, output is 20ft. Totals are 48ft and 49ft, within 3% for voltage drop. However, you've got an 11ft difference in your inputs, and a 10ft difference in your outputs, which would be way off. Alternatively, you can switch the breaker layout so that your UPS1 I/O lengths are 23/25ft, and UPS2 I/O lengths are 24ft/24ft, with totals at 48ft/48ft which is definitely okay for voltage drop.
Are they both right and the alt install unnecessary? Or are the drawings wrong?